Failed 14-50

PDACPA

Well-Known Member
First Name
PDA
Joined
Feb 21, 2020
Threads
23
Messages
992
Reaction score
411
Location
Tampa, FL
Vehicles
2021 Taycan RWD, 1989 911 Carrera
Country flag
Got home yesterday with 25% battery remaining and put it on my Chargepoint Homeflex and selected Direct Charging while I ate dinner and planned to turn off when I went to take out the trash. I just wanted to get a little charge on there in case I had to run out and then would let the planner charge to 80% overnight. I happened to hit the app and noticed the red error charging and it had only charged for a few minutes. Walked to the garage and here is what I found. Yes I know, the Hubbell is the recommended receptacle, but my electrician had installed a Leviton and I never unplug the Chargpoint and it has worked for 3.5 years.

Unfortunately it melted some of the Chargepoint plug as well as the receptacle. My question is, though the wiring sheath melted near the receptacle, can I cut off the wire and install a new receptacle? I have enough wire to do so or do I need to run new wire. The breaker appears fine.

Thanks

Porsche Taycan Failed 14-50 image0


Porsche Taycan Failed 14-50 image2


Porsche Taycan Failed 14-50 image3


Porsche Taycan Failed 14-50 image5
Sponsored

 

daveo4EV

Well-Known Member
First Name
David
Joined
Jan 28, 2019
Threads
192
Messages
7,003
Reaction score
10,473
Location
Santa Cruz
Vehicles
Cayenne Hybrid, 911(s) GT3/Convertable
Country flag
Got home yesterday with 25% battery remaining and put it on my Chargepoint Homeflex and selected Direct Charging while I ate dinner and planned to turn off when I went to take out the trash. I just wanted to get a little charge on there in case I had to run out and then would let the planner charge to 80% overnight. I happened to hit the app and noticed the red error charging and it had only charged for a few minutes. Walked to the garage and here is what I found. Yes I know, the Hubbell is the recommended receptacle, but my electrician had installed a Leviton and I never unplug the Chargpoint and it has worked for 3.5 years.

Unfortunately it melted some of the Chargepoint plug as well as the receptacle. My question is, though the wiring sheath melted near the receptacle, can I cut off the wire and install a new receptacle? I have enough wire to do so or do I need to run new wire. The breaker appears fine.

Thanks

image0.jpeg


image2.jpeg


image3.jpeg


image5.jpeg
not a Hubble industrial rated NEMA 14-50 outlet - but yeah that's pretty bad…

see Porsche's tech bulletin here: hubble part number provided - accept no substitutes…

https://www.taycanforum.com/forum/t...-related-porsche-ntsb-article-analysis.13902/
https://static.nhtsa.gov/odi/tsbs/2022/MC-10222530-0001.pdf
 

daveo4EV

Well-Known Member
First Name
David
Joined
Jan 28, 2019
Threads
192
Messages
7,003
Reaction score
10,473
Location
Santa Cruz
Vehicles
Cayenne Hybrid, 911(s) GT3/Convertable
Country flag
Got home yesterday with 25% battery remaining and put it on my Chargepoint Homeflex and selected Direct Charging while I ate dinner and planned to turn off when I went to take out the trash. I just wanted to get a little charge on there in case I had to run out and then would let the planner charge to 80% overnight. I happened to hit the app and noticed the red error charging and it had only charged for a few minutes. Walked to the garage and here is what I found. Yes I know, the Hubbell is the recommended receptacle, but my electrician had installed a Leviton and I never unplug the Chargpoint and it has worked for 3.5 years.

Unfortunately it melted some of the Chargepoint plug as well as the receptacle. My question is, though the wiring sheath melted near the receptacle, can I cut off the wire and install a new receptacle? I have enough wire to do so or do I need to run new wire. The breaker appears fine.

Thanks

image0.jpeg


image2.jpeg


image3.jpeg


image5.jpeg
I would confirm your ChargePoint flex is configured correctly - they can pull 50 amps - the correct setting for ChargePoint flex with NEMA 14-50 outlet is 50 amp breaker and 40 amp charge rate (9.6 kW raw power)

if you have enough wire you can replace the socket with an industrial grade socket - see part number's provided by Porsche's tech bulletin linked above - or you could hardiwre the ChargePoint and avoid this problem all together…
 

hifi239

Well-Known Member
First Name
Will
Joined
Mar 15, 2023
Threads
27
Messages
470
Reaction score
423
Location
Boston
Vehicles
Taycan
Country flag
Wow, that's ugly! It's not clear what actually failed, and given that, it might be better to pull new wire. You own two Porsches, one extremely valuable and probably in the same garage. I'd have an electrician pull new 6 AWG wire. The conduit is in place and there is existing wire, the pull might be easy. Then 1) connect to a new Hubbell, or better yet, 2) hardwire the flex and put in a 60A breaker and you can go up to 48A. What's the Flex plug look like?
 

philbur

Well-Known Member
First Name
Phil
Joined
Mar 30, 2021
Threads
6
Messages
341
Reaction score
332
Location
Seattle
Vehicles
1997 911 C2 (993), 2015 Cayenne S, 1978 VW Bus
Country flag
I also see electrical tape wrapped around the plug? That looks sloppy to me. Should install with no additional items and def an industrial plug. I replaced my neighbors as his was tripping once in a while and when I went to look at it it was all white and heat cycled - tesla charger.
 


OP
OP
PDACPA

PDACPA

Well-Known Member
First Name
PDA
Joined
Feb 21, 2020
Threads
23
Messages
992
Reaction score
411
Location
Tampa, FL
Vehicles
2021 Taycan RWD, 1989 911 Carrera
Country flag
I would confirm your ChargePoint flex is configured correctly - they can pull 50 amps - the correct setting for ChargePoint flex with NEMA 14-50 outlet is 50 amp breaker and 40 amp charge rate (9.6 kW raw power)

if you have enough wire you can replace the socket with an industrial grade socket - see part number's provided by Porsche's tech bulletin linked above - or you could hardiwre the ChargePoint and avoid this problem all together…
Thanks Dave. Yes I had my ChargePoint configured correctly. Was pulling 8.7kW per the app.

My ChargePoint was not the hardwired version (but with the plug melted not sure it even works at this point), but I did wonder if I could just convert it to hardwired.
 
OP
OP
PDACPA

PDACPA

Well-Known Member
First Name
PDA
Joined
Feb 21, 2020
Threads
23
Messages
992
Reaction score
411
Location
Tampa, FL
Vehicles
2021 Taycan RWD, 1989 911 Carrera
Country flag
Wow, that's ugly! It's not clear what actually failed, and given that, it might be better to pull new wire. You own two Porsches, one extremely valuable and probably in the same garage. I'd have an electrician pull new 6 AWG wire. The conduit is in place and there is existing wire, the pull might be easy. Then 1) connect to a new Hubbell, or better yet, 2) hardwire the flex and put in a 60A breaker and you can go up to 48A. What's the Flex plug look like?
Here is the Flex Plug.

Porsche Taycan Failed 14-50 image1
 

hifi239

Well-Known Member
First Name
Will
Joined
Mar 15, 2023
Threads
27
Messages
470
Reaction score
423
Location
Boston
Vehicles
Taycan
Country flag
could just convert it to hardwired
My understanding is that the ChargePoint Flex 14-50 is one of the few EVSE that can be converted to hardwired. I'd do that.
 


OP
OP
PDACPA

PDACPA

Well-Known Member
First Name
PDA
Joined
Feb 21, 2020
Threads
23
Messages
992
Reaction score
411
Location
Tampa, FL
Vehicles
2021 Taycan RWD, 1989 911 Carrera
Country flag
I would confirm your ChargePoint flex is configured correctly - they can pull 50 amps - the correct setting for ChargePoint flex with NEMA 14-50 outlet is 50 amp breaker and 40 amp charge rate (9.6 kW raw power)

if you have enough wire you can replace the socket with an industrial grade socket - see part number's provided by Porsche's tech bulletin linked above - or you could hardiwre the ChargePoint and avoid this problem all together…
Question about what should happen when this occurs.

Should the breaker trip? Mine did not. It is wired to my main panel where the power company power comes in and that panel has 3 breakers (one for the HVAC, one for the Main Panel in the garage for all the house) and one for the EV Chargers.

The Chargepoint lights went out. Car showed red on charge screen "error charging." I noticed the burn mark on the cover plate of the receptacle and then turned the breaker off and proceeded to unplug and unscrew. ChargePoint and Porsche App did not send a notification either.
 
OP
OP
PDACPA

PDACPA

Well-Known Member
First Name
PDA
Joined
Feb 21, 2020
Threads
23
Messages
992
Reaction score
411
Location
Tampa, FL
Vehicles
2021 Taycan RWD, 1989 911 Carrera
Country flag
My understanding is that the ChargePoint Flex 14-50 is one of the few EVSE that can be converted to hardwired. I'd do that.
I just pulled up some pictures of it (I'm at work) and looks like the plug can be disconnected and I can wire it direct. I think I might just go that route if I can determine if the ChargePoint was not impacted by the melted plug.
 

DerekS

Well-Known Member
First Name
Derek
Joined
May 25, 2021
Threads
119
Messages
3,214
Reaction score
5,530
Location
Los Gatos, CA
Vehicles
2025 Taycan GTS
Country flag
If it were me I wouldn't want to reuse any of the items in the chain, here.

Not the Chargepoint and definitely not the wiring.

Call an electrician - not the one who did this in the first place - and have them run a new home-run to the breaker, new Hubble (or new hardwired EVSE) etc.

I just don't think it's worth taking chances with.
 

Wakesurfer

Well-Known Member
First Name
Bob
Joined
Nov 19, 2020
Threads
4
Messages
244
Reaction score
306
Location
Granbury, Texas
Vehicles
2021 Taycan 4S, 2023 YukonXL, 2024 Macan S
Country flag
If it were me I wouldn't want to reuse any of the items in the chain, here.

Not the Chargepoint and definitely not the wiring.

Call an electrician - not the one who did this in the first place - and have them run a new home-run to the breaker, new Hubble (or new hardwired EVSE) etc.

I just don't think it's worth taking chances with.
What he said!!!☝
 

trycan

Well-Known Member
Joined
Jul 24, 2023
Threads
8
Messages
330
Reaction score
225
Location
Boston
Vehicles
2025 Taycan 4S+ w/ Active Ride (Scale 1:1), Taycan Turbo S (Scale: 1:43)
Country flag
Should the breaker trip? Mine did not
If you had a GFCI breaker on the circuit, yes it would have tripped very quickly in this situation and likely avoided all the melting. However, the Chargepoint likely also has a GFI internally, and having both GFIs protecting the circuit can cause nuisance tripping (i.e. no actual problem).
GFCI breakers on the NEMA 14-50 outlets is a relatively new code requirement (last 5-yrs depending on your local regulations).
You could swap into a GFCI breaker and try the same wiring run again, or call the electrician like mentioned above and have them look at everything to make it right.
 

Jhenson29

Well-Known Member
First Name
Jeremy
Joined
Feb 9, 2021
Threads
37
Messages
3,014
Reaction score
4,650
Location
St. Louis, MO
Vehicles
2022 Macan S; 2021 Taycan 4S
Country flag
I’ve been doing industrial electrical work for almost 20 years. I just had my NFPA 70E refresh training this morning, actually.

When we have charred wires in the field (typically from loose connections causing excessive heat from resistance, but occasionally from an arc) we typically just cut the wire and strip the insulation back past the point the of damage. It’s unlikely the entire cable needs to be replaced. In fact, I’ve never replaced an entire conductor due to charring at a connection, unless there wasn’t enough to reuse. You can always ohm the wires end to end if you want. Easiest way is to connect them together on one end and then check continuity between them on the other. It should be very low. Likely 0.2 ohms or less depending on how long your branch circuit is.

That said, it’s hard to tell how far back the insulation is damaged from the pictures. It’s hard to tell, but the wires look a little long to begin with. Cramming wires in a box, either because they’re too long or the box is too small (or both) means the heat may damage other parts of the wire pressed against it. Most of what I work on doesn’t have that issue.

Assuming the EVSE powers up after the plug is replaced or is hard-wired, I would think it’s probably fine.

I don’t know that I would expect the breaker to trip unless there was a direct short. I see lots of melting, but it’s not clear that anything is actually shorted. The melting itself would likely be from a poor connection which has increased resistance, causes a voltage drop, and dissipates heat. The current may have been within spec, and the circuit may have opened at the plug prior to shorting. Not sure.
 

Jhenson29

Well-Known Member
First Name
Jeremy
Joined
Feb 9, 2021
Threads
37
Messages
3,014
Reaction score
4,650
Location
St. Louis, MO
Vehicles
2022 Macan S; 2021 Taycan 4S
Country flag
In any case….I wouldn’t reuse the receptacle….?