David Bennett
Well-Known Member
- Joined
- Mar 9, 2021
- Threads
- 8
- Messages
- 108
- Reaction score
- 108
- Location
- UK
- Vehicles
- Taycan 4S, Golf 8r

There are circumstances where a 40A for a 7KW EVSE would be right for the UK. Typically this would be if you where you had an additional circuit installed in an already well populated consumer unit. The combined heating effect would lead to the kind of de rating we were discussing earlier (it's in the standards and the wiring regs). If you are installing an additional feed direct from the meter serving only the ESVE then no derating is required (unless the ambient temperature is very high) and you will only need 32A for a 7KW ESVE. I don't see how a 7KW load will draw 38A unless I am missing something. If it was a very short term event (few minutes) it still won't trip the breaker but you don't want to be relying on that.Interesting. My breaker is 40A. The man who did the survey in advance of fitting told me that sometimes the current can go up as high as 38A as the car comes off charge or at some point of the charge process. I didn’t really understand why that would be and if your 32A circuit has never tripped then maybe he was wrong. But 32A is a pretty fine margin on a 7.1kW EVSE